Service GEC

mannyb

Senior Member
Location
Florida
Occupation
Electrician
I searched a couple topics but nothing really clarified. I have a few books but cant really narrow down the address in NEC. Is the GEC at Service disconnect need to be on same buss as neutral or equipment frame? I recently ran service call at a multi family dwelling I noticed a common GEC wire tied to each service disconnect with mechanical lug per disconnect
 
Is the GEC at Service disconnect need to be on same buss as neutral or equipment frame?
It must terminate to the neutral if the MBJ is a screw or bonding strap. If the MBJ is a wire or bus type then the GEC can terminate to the EGC bus/frame.

I recently ran service call at a multi family dwelling I noticed a common GEC wire tied to each service disconnect with mechanical lug per disconnect
It may or may not be code compliant you would need to provide more details. There is a GEC connection with a lug at each service disconnect but what's on the other end of the GEC?
 
It must terminate to the neutral if the MBJ is a screw or bonding strap. If the MBJ is a wire or bus type then the GEC can terminate to the EGC bus/frame.


It may or may not be code compliant you would need to provide more details. There is a GEC connection with a lug at each service disconnect but what's on the other end of the GEC?

Each disconnect frame has a mechanical lug and the #6 runs through Each no slices. The ground rod has an acorn clamp
 
  • Like
Reactions: J2H
It must terminate to the neutral if the MBJ is a screw or bonding strap. If the MBJ is a wire or bus type then the GEC can terminate to the EGC bus/frame.


It may or may not be code compliant you would need to provide more details. There is a GEC connection with a lug at each service disconnect but what's on the other end of the GEC?

Can you provide address in NEC that mentions if screw or strap it goes to neutral bar
 