m2oliva

Member
I have a situation where the power companies transformer is about 300 ft from the panel we are feeding. Due to wall space problems the meter is being placed by the trans along with a 200 amp main breaker . The panel at the building now becomes a sub panel. So my question is , do i have to install 2 ground rods at the main panel and no gec at the sub panel. There is no water in the new building,but there is a concrete enclosed electrode allready installed?
 
Re: service gec

What type of raceway is being used between the meter disconnect and the building? Are you installing an EGC with the feeder? No matter what, you need a grounding electrode system at both the building and meter locations?
Don
 
Re: service gec

Were using direct burial with an egc.ALso when installing the meter and disc in an open field,is there specific material the the power co. makes you use for mounting.Is two posts w /some type of pressure treated wood between acceptable?Thanks in advance
 
Re: service gec

Come on now, don't drop down in size for the fault clearing conductor.

Use the neutral, or better yet parallel both the neutral and equipment ground wire.

Now yell at me, but back up with the math.
 
Re: service gec

Originally posted by bennie:
Now yell at me, but back up with the math.
I'm not going to yell, but I will do some math, will all values from the NEC [310.15(B)(6)], 310.16, 250.122, table 8 of chapter 9.
Here goes:

2/0 copper ungrounded feeder circuit with 6 AWG EGC at 300'. Total resistance of circuit conductors is 0.1764 Ohms. Maximum line to ground voltage: 120V. 120/0.1764= 680A

Will 680 Amps safely and quickly initiate a 200 breaker?

I agree that a full sized fault clearing conductor (such as the nuetral) will do a better job (2,068Amps), but will the above scenario not work?
 
Re: service gec

"Is two posts w /some type of pressure treated wood between acceptable?" This question can only be answered by the POCO. Where I am, we can't mount a meter on a pressure treated post, it has to be metal strut, with a concrete pad in front.
I always liked using 10 ft PT posts, 6x6, that gives you 5 ft in the ground, 3 feet below the bottom of the ditch, so it stands up while the service is being installed. Now its strut and concrete, takes more time to install, not always better. But the POCO has probably seen meters installed on 2x4 that fall over..
 