Alright gang, it's been a while since I've haunted this forum. But I've been run around and incurred some serious brain damage on a local project here in Colorado. Here XCEL requires a cold sequence disconnect on services 320A and less if the fault at the meter is in excess of 10kAIC, and the XCEL standards state that the cold sequence disconnect shall be treated as a meter disconnect per NEC. NEC 230.82(3) states that the meter disconnect be labelled "Meter Disconnect Not Service Equipment" (though I'd argue it's service equipment, but not the service disconnect. 250.82(3) allows for a meter disconnect, but requires that it is grounded and bonded per Parts VII and V of Article 250. 250.142 allows for the grounded conductor to be use for equipment grounding on the supply side of service equipment. So far, clear as can be. As we progress thru code review, NEC 250.24 allows the connection to grounding electrode (GEC) at any point from the load end of the service lateral to the service disconnecting means. So it can be done inside the cold sequence disconnect, and I believe we could bond the neutral here. All fairly clear in my mind.
Here's where it gets tricky. This project has the cold sequence disconnect and meter built on a rack per XCEL dwg SC-50. XCEL requires a ground rod be driven at this rack. There is a feeder (not branch circuit) run to a separate building or structure where there is an exterior disconnect labelled service disconnect. It feeds (back to back) a MLO panel. I view that the bond takes place in the cold sequence disconnect, and a 4-wire feeder runs from the meter to the exterior service disconnect. I argue that I am required to have a GEC at the exterior service disconnect and that the bond is not made here (per NEC 250.32(B) (see also Exhibit 250.19).
I don't think it's correct to use the grounded conductor to ground all the way to the service disconnect. What say you all? FYI - it would've been nice if we could've built the service on the building exterior, but that ship has sailed. I could also put the service disconnect on the rack (the rack would house cold seq disco, meter and service disco) - this would be more obvious that the structure is a separate structure and needs a GEC per 250.32.
It's not real clear why the building permit is being held up. I believe 250.24 allows me to bond any place between the lateral and main service disconnect. I don't think this scenario creates a parallel neutral, but maybe I'm too close to it.
Any feedback is greatly appreciated. If I'm lucky, the AHJ for the project will be scanning the forum and we can resolve this ASAP.
Thank so much, and Happy New Year!
Here's where it gets tricky. This project has the cold sequence disconnect and meter built on a rack per XCEL dwg SC-50. XCEL requires a ground rod be driven at this rack. There is a feeder (not branch circuit) run to a separate building or structure where there is an exterior disconnect labelled service disconnect. It feeds (back to back) a MLO panel. I view that the bond takes place in the cold sequence disconnect, and a 4-wire feeder runs from the meter to the exterior service disconnect. I argue that I am required to have a GEC at the exterior service disconnect and that the bond is not made here (per NEC 250.32(B) (see also Exhibit 250.19).
I don't think it's correct to use the grounded conductor to ground all the way to the service disconnect. What say you all? FYI - it would've been nice if we could've built the service on the building exterior, but that ship has sailed. I could also put the service disconnect on the rack (the rack would house cold seq disco, meter and service disco) - this would be more obvious that the structure is a separate structure and needs a GEC per 250.32.
It's not real clear why the building permit is being held up. I believe 250.24 allows me to bond any place between the lateral and main service disconnect. I don't think this scenario creates a parallel neutral, but maybe I'm too close to it.
Any feedback is greatly appreciated. If I'm lucky, the AHJ for the project will be scanning the forum and we can resolve this ASAP.