Have you read through 250.122?
Roger
Wouldn't 250.66 apply here?
Have you read through 250.122?
Roger
Wouldn't 250.66 apply here?
Yes I know what 250.122 states, its for grounding conductors for grounding equipment and raceways. My questions is if they are paralled wires do you have to size wire according to circular mills, this is what an inspector told me...??
Yes I know what 250.122 states, its for grounding conductors for grounding equipment and raceways. My questions is if they are paralled wires do you have to size wire according to circular mills, this is what an inspector told me...??
What I believe you have is two 200A service panels. There are two ways to run a GEC, either as 1) separate GEC for each panel or 2) a common GEC for both. On the latter, you can tap down to individual GEC size for each panel.... My questions is if they are paralled wires do you have to size wire according to circular mills, this is what an inspector told me...??
Good Morning
If you have a residential home with 120/240 volts single phase 400 amp service with 2 - 200 amp panels fed off one 400 amp service meter with separate 4/0 SER what size ground wire is ran for grounding electrodes (rods) and to water main.
Each 4/0 AL SER is a Service Entrance Conductor. The "main power feeder" stipulation only applies on the load side of a service disconnect.4/0 ser is not to code. The 4/0 exception applies to a single 200 amp residential service. You have a 400 amp service. The 200 amp panels would require 3/0 copper or 250 mcm aluminum. 'least that's the way it is in SW Florida. Let the beating begin!
Do you size it for paralleled 4/0 by circular mills...
My questions is if they are paralled wires do you have to size wire according to circular mills, this is what an inspector told me...??
4/0 ser is not to code. The 4/0 exception applies to a single 200 amp residential service. You have a 400 amp service. The 200 amp panels would require 3/0 copper or 250 mcm aluminum. 'least that's the way it is in SW Florida. Let the beating begin!
What I believe you have is two 200A service panels. There are two ways to run a GEC, either as 1) separate GEC for each panel or 2) a common GEC for both. On the latter, you can tap down to individual GEC size for each panel.
That said, individual GEC is sized to 4/0 Al (#4 copper, #2 Al), common is sized to sum of cmils (#2 copper, 1/0 Al).
Questions for Big Guns... right?I'm confused, what size conductors are feeding the meter?
Aslo why SER?
Questions for Big Guns... right?
infinity;1454917 said:Questions for Big Guns... right?I'm confused, what size conductors are feeding the meter?
Also why SER?
Had to go back to the OP (meaning both original poster and original post in this case) and see why you guys were asking instead of answering. Now I see why.I would assume so.
The two 4/0 are not parallel but separate service entrance conductors. As I stated earlier, you'd use the sum (423200cmils) to size a common GEC and/or use 4/0 to size individual GEC's.A little confusion at the beginning of this thread.
250.66 is for sizing grounding electrode conductors and is based on largest service entrance conductor or equivalent.
250.122 is for sizing equipment grounding conductors and is based on the largest overcurrent protective device that may energize the conductor in question.
OP appears to be asking about grounding electrode conductors so 250.66 is what applies.
Isn't the "equivalent" largest service entrance conductor in OP 2-#4/0 AWG (aluminum?) conductors which is equal to 423200 circular mils?
250.66 tells us this will need #2 copper or 1/0 aluminum GEC.