Service grounding

Darho

Member
Location
Cookeville
Occupation
Electrician
So concerning the post in facebook about service grounding. If you ground the meter can and rely on the neutral to be the bond jumper between the meter and the disconnect as the diagram illustrates. What happens if by chance you lose your neutral between the meter can and the disconnect? Where does the voltage return to. There is no ground conductor anymore so wouldn’t all grounded metal appliances then become charged by the current seeking to go to ground?
 
So concerning the post in facebook about service grounding. If you ground the meter can and rely on the neutral to be the bond jumper between the meter and the disconnect as the diagram illustrates. What happens if by chance you lose your neutral between the meter can and the disconnect? Where does the voltage return to. There is no ground conductor anymore so wouldn’t all grounded metal appliances then become charged by the current seeking to go to ground?
Yes, everything connected to the grounding system will be energized, but the same thing happens if you lose your service neutral and that is much more likely than losing the neutral between the mete and the disconnect.

Also the current is not trying to go to ground, it is trying to go back to the source. On a grounded system the earth is a path back to the source, and some current will flow on that path.
 
So concerning the post in facebook about service grounding. If you ground the meter can and rely on the neutral to be the bond jumper between the meter and the disconnect as the diagram illustrates. What happens if by chance you lose your neutral between the meter can and the disconnect? Where does the voltage return to. There is no ground conductor anymore so wouldn’t all grounded metal appliances then become charged by the current seeking to go to ground?
Even if there were a GEC connected in the main panel, if the neutral was broken, ahead of the main panel, everything would still become energized. A Grounding electrode will not do anything for a broken neutral.
 
Even if there were a GEC connected in the main panel, if the neutral was broken, ahead of the main panel, everything would still become energized. A Grounding electrode will not do anything for a broken neutral.
In my area where the municipal water piping system is copper the grounding electrode conductor will serve as the neutral. If the neutral is lost current will flow through the municipal water system finding a way back to the source

There are countless bad neutrals out there and the neutral current is flowing on the copper piping system looking for a path back. The neutral for House A might be the neutral for House B and House C

Its at a point now when doing a service change, I will tell guys to put a amprobe on the water pipe GEC to check the current draw as guys are surprised when the old GEC is removed there is a large spark. Municipal water system carry a lot of current
 