GRC up through the soffit and roof.
Make it so the upper window sash can not be lowered.What do you think.
Backup and show us the whole side of the house.
-Hal
230.9 Clearances on Buildings. Service conductors and final
spans shall comply with 230.9(A), (B), and (C).
(A) Clearances. Service conductors installed as open conductors
or multiconductor cable without an overall outer jacket
shall have a clearance of not less than 900 mm (3 ft) from
windows that are designed to be opened, doors, porches, balconies,
ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be
permitted to be less than the 900 mm (3 ft) requirement.
NEC doesn't mention windows it mentions building openings. If the upper portion isn't operable the only opening is the lower portion. A window that doesn't open at all doesn't have any clearance requirements from open service conductors.Where is the wording in the NEC about the upper window being inoperable?
Yes, several times, inspector approved.Larry - have you done that with a window before and how did you do it
but the overhead looks too tight to the window from the photo for my liking.
Like 480 said, through the roof.
Compared to two screws, with labor? :happysad:I would just go through the eve and roof because that's the easiest. Conduit,weather-head and boot isn't that expensive.
I would just go through the eve and roof because that's the easiest. Conduit,weather-head and boot isn't that expensive.
Compared to two screws, with labor? :happysad:
Or does someone want to do the work?