gporter
- NW Pennsylvania
Here is the situation. This is a commercial compound of 6 separate buildings. There is a central POCO transformer, and each building is to be supplied from this transformer by buried service entrance conductors, each building has its own disconnect and grounding. The owner would like one meter to cover all buildings, and POCO can supply CT metering at the transformer. One set of service lateral conductors will come out of the transformer, through the CT meter, and to large ?Polaris? connectors where the services to the various buildings are tapped.
The question is ? Is it true that once the service LATERAL goes thru the meter transformer coils they become service entrance conductors and not laterals? NEC 230.40 says that each service lateral shall supply only one set of service entrance conductors. So now we can?t split out to feed six separate buildings. However, if we had separate meters at each of the buildings, it would be considered six separate service laterals, and everything would be OK. Why does moving the metering point to a central location change anything?
Thansks, Greg
Thansks, Greg