ceb58
Senior Member
- Location
- Raeford, NC
Looking at plans for an addition to a church with an existing CT can feeding 2- 200 amp 240v single phase panels . The only thing the engineer has on the plans is the load calculation for a new 200 amp 240v single phase panel that is to be added. His load calc. is 41.6 Kw for this new panel alone ( will never see 100amps let alone 173 amps but what ever ). I called the POCO and got the max demand load on this church for the last year per 220.87 (1). It was a whopping 6.5 Kw. So with these numbers it works out at 200.08 amps demand. Any reason I cannot just up it to 320 amp service and call it a day. I have to replace the CT can any way due to having to relocate it and it did receive some damage from the hurricane last year.