What is the height requirement for the mast above the roof for 2" Conduit? The conduit punches through the overhang and out through the roof.
As has been said, check with your POCO. Here, if we penetrate the roof, we must use 2-1/2" rigid. If we go a certain height above the roof we have to brace or guy it. The height is POCO dictated. Some start at 36", some at 42" above roof.What is the height requirement for the mast above the roof for 2" Conduit? The conduit punches through the overhang and out through the roof.