Pitkin County in Colorado requires construction of residential services over 400 A to be designed and stamped by a P.E. Also, the utility requires a hot sequence meter socket with associated disconnect switch within 2 feet of the meter. For the disconnect switches the electrical contractor wanted 800 A gear with 2 circuit breakers and a CT enclosure for the meter. He also had two fused disconnects at the house 200 ft away from the meter, which my 1-line drawing showed as the service disconnects. The AHJ ruled that the service disconnects needed to be the 2 circuit breakers at the meter, based on their interpretation of 250.30. Therefore they wanted the GEC to be run 200 ft to the meter/disconnect gear before bonding to the neutral.
I pointed out that 250.30 only applies to separately derived systems, of which services were explicitly excluded per Article 100 Definitions. I also stated it was poor engineering practice to run a GEC 200 ft before ground fault current was returned to the neutral. However, they refused to listen to me as they had already made their decision.
Any opinions of the AHJ ruling?
I pointed out that 250.30 only applies to separately derived systems, of which services were explicitly excluded per Article 100 Definitions. I also stated it was poor engineering practice to run a GEC 200 ft before ground fault current was returned to the neutral. However, they refused to listen to me as they had already made their decision.