Got a test question not sure how to answer: "A 120/240-volt, 200-ampere service requires a neutral with a minimum ampacity of:".
Answers to choose from are: 140 160 175 or 200 amps.
At first I thought well 230.42 Exception says" Grounded conductors not connected to a OC device shall be permitted to be sized at 100% of non and continuous load so that would be 200 amps. However...
230.42C says "The grounded conductor shall not be smaller than required by 250.24C which says it can't be smaller than the GEC in table 250.66. Table 250.66 gives wire sizes based on the Largest ungrounded service conductor, but it does not chart minimum ampacities and the question doesn't say the type of cable or even if it's residential. So how do I determine the "minimum ampacity" of the service neutral? And then there is 220.61 which says the service neutral load shall be the max unbalanced load between any one ungrounded conductor and neutral, so wouldn't that be 100 amps in a 200 amp service?
What am I missing?
Answers to choose from are: 140 160 175 or 200 amps.
At first I thought well 230.42 Exception says" Grounded conductors not connected to a OC device shall be permitted to be sized at 100% of non and continuous load so that would be 200 amps. However...
230.42C says "The grounded conductor shall not be smaller than required by 250.24C which says it can't be smaller than the GEC in table 250.66. Table 250.66 gives wire sizes based on the Largest ungrounded service conductor, but it does not chart minimum ampacities and the question doesn't say the type of cable or even if it's residential. So how do I determine the "minimum ampacity" of the service neutral? And then there is 220.61 which says the service neutral load shall be the max unbalanced load between any one ungrounded conductor and neutral, so wouldn't that be 100 amps in a 200 amp service?
What am I missing?