hitehm
Senior Member
- Location
- Las Vegas NV
The writer is definitely using the 70% rule in 220.61 but even if he provided the needed info to apply that section he is still wrong because as it reads: "That portion of the unbalanced load in excess of 200 amperes" He's applying 70% against the entire 200 amp service. It would only apply to the portion above 200 amps. To me it seems like an all around misinterpretation of the code.