Hello,
I am doing a house with a Detached Garage.
I would like to do a 200a 8/16 pass thru panel on the garage and feed 200 a UG to the house. Would I be required to provide a disco on the house. The feeders will be protected via the 200a main on the pass thru at the garage. I do not think I am required since the wires are protected but was looking at 230.70(A)(1)??
Lets get this figured out and then talk about where the cold water could land
House panel is in the basement BTW
I am doing a house with a Detached Garage.
I would like to do a 200a 8/16 pass thru panel on the garage and feed 200 a UG to the house. Would I be required to provide a disco on the house. The feeders will be protected via the 200a main on the pass thru at the garage. I do not think I am required since the wires are protected but was looking at 230.70(A)(1)??