Not to sure and having trouble finding it, but here it goes. Can you run a 12/3 for an ac unit in attic 240v system and supply the service outlet off of one of those legs with neutral?
ddubbs103 said:Not to sure and having trouble finding it, but here it goes. Can you run a 12/3 for an ac unit in attic 240v system and supply the service outlet off of one of those legs with neutral?
Even if you made the repairs by running cords for the repair, you still wouldn't have a working AC.buckofdurham said:If the ac trips the breaker and needs repairs. You have no power in attic.
M. D. said:this question was made for you I think:-?
http://www.necplus.org/Lists/CodeTopic/DispForm.aspx?ID=9
A 20-A, 240-V nonfused disconnect for an air handler rated for 7.6 amperes is installed in the unfinished attic space of a dwelling unit. The 2-pole breaker is located in the basement panel. To install a duplex receptacle for servicing, can a 3-wire circuit (two ungrounded conductors and a neutral) be run to the nonfused disconnect, and one of the ungrounded conductors as well as the grounded conductor be used to feed the receptacle on the line side of the disconnect?
Answer
In accordance with 210.4(C), this type of multiwire circuit is permitted to supply the line-to-line load and the line-to-neutral load. Because the receptacle is being supplied on the line side of the ac unit disconnecting means, it is in compliance with the requirement of 210.63.
The fact that the ac unit load is 7.6 amperes allows the receptacle outlet to also be supplied by this branch circuit, per 210.23(A)(2). The nameplate on the ac unit must permit the overcurrent protection to be sized at 20 amperes for this to work. The installation of a fused-disconnect at the ac unit does not make a difference, as the conductors from the panelboard to the disconnect, fused or nonfused, are branch-circuit conductors protected by the 20-ampere, 2-pole overcurrent protective device installed at the panelboard.
2008 NEC said:422.12 Central Heating Equipment.
Central heating equipment other than fixed electric space-heating equipment shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump, valve, humidifier, or electrostatic air cleaner directly associated with the heating equipment, shall be permitted to be connected to the same branch circuit.
Exception No. 2: Permanently connected air-conditioning equipment shall be permitted to be connected to the same branch circuit.
buckofdurham said:Would that be true for a well pump. And the light in the well house
LarryFine said:You could also install a small panel .
iwire said:I have no idea why people are saying 'not to do it at my house'
iwire said:On commercial RTUs (Roof Top Units) most now come to the job with a factory installed service receptacle supplied by the feeder to the unit.