Second time in 3 months, am I missing something? 200 amp main panel with disconnect, appears to have a split neutral bar ( one on each side of the breakers joined by a jumper bar). All the conductors are romex. All the neutrals are on one neutral bus bar, all the grounds are on the other neutarl bus bar. The bus bar with all the neutrals is bonded to the can, the bus is also connected to main feeder neutral. The bus bar with all the gounds is connected to the ground wire that goes to the water service, this bus bar is not bonded to the can. Problem....the electrician removed the jumper bar that would connect the two bus bars together. I was under the impression that the grounds and neutral where suppose to be isolated from each other only if this panel was a sub-panel. Is this right or wrong........referance to the code?
Thanks