I’m upgrading a service from 200 to 320/400 amp.
We are currently under the 2017 for single family dwelling so I’m not required to have exterior disconnects.
Room is tight so I was going to do away with exterior disconnects, but inspector said in this jurisdiction they adhere to to the 5’ rule or 2 stud bay rule unprotected conductors. Which caused me to send him an email about my plan which he says is a cod violation so I will lay it out for you. Please tell me the code if it’s wrong.
I was going to mount the 320 meter outside nipple over about 12” in 2.5” into an exterior jbox slash trough (using this instead of 3” LB) pulling both sets of feeders in this 2.5”.
From the back of the exterior box I was going 16” into a 2’ x 2’ x 8” jbox and then I was going to leave there with 2- 2” going to the 200 amp main breaker panels.
Inspector says I can’t (or he doesn’t think I can ) leave the 320!meter with both sets of wires in the same conduit.
You guys see a problem with that?
We are currently under the 2017 for single family dwelling so I’m not required to have exterior disconnects.
Room is tight so I was going to do away with exterior disconnects, but inspector said in this jurisdiction they adhere to to the 5’ rule or 2 stud bay rule unprotected conductors. Which caused me to send him an email about my plan which he says is a cod violation so I will lay it out for you. Please tell me the code if it’s wrong.
I was going to mount the 320 meter outside nipple over about 12” in 2.5” into an exterior jbox slash trough (using this instead of 3” LB) pulling both sets of feeders in this 2.5”.
From the back of the exterior box I was going 16” into a 2’ x 2’ x 8” jbox and then I was going to leave there with 2- 2” going to the 200 amp main breaker panels.
Inspector says I can’t (or he doesn’t think I can ) leave the 320!meter with both sets of wires in the same conduit.
You guys see a problem with that?