Attached sketch shows service rated switchboard fed from local electric utility conductors.
The switch has two main service disconnects in compartment #1 and compartment #2.
I have plans that show each compartment #1 and #2 has neutral to ground bond i.e main bonding jumper.
It is one ul listed assembly switchboard. I find this odd because usually they comply with 250.24(B) exception 1 you have one main bonding jumper for the whole assembly.
Has anyone seem something like below? Can below be done and be compliant with code?
The switch has two main service disconnects in compartment #1 and compartment #2.
I have plans that show each compartment #1 and #2 has neutral to ground bond i.e main bonding jumper.
It is one ul listed assembly switchboard. I find this odd because usually they comply with 250.24(B) exception 1 you have one main bonding jumper for the whole assembly.
Has anyone seem something like below? Can below be done and be compliant with code?