This is definately a silly question to be asking, but I need some input on this to back my position.
I have a situation where an outside firm is completing some AC power audits on various panels. They have comeback saying that every panel surveyed will need to be upgraded.
The basis for this statement is their method of calculating the loads. The person making the calculations says that NEC requires the circuit to be loaded no more than 80% of its OCP value. (ie - 20A breaker can not exceed a 16A load) This I agree with when sizing OCP devices and wire. However, when it comes to a load study, I am more interested in the actual values rather than what the circuit can handle. Thus, if a circuit is protected by 30A breaker, and the connected load is only 17A. The 17A should be used in the calculation, not 24A.
Any opinion on this?
Conversely, the same problem with the service. I have always understood that the service should not be loaded to more than 80% of its rating. Can anyone point out a NEC reference for this? I am at a loss. The loading is actual load, not calculated load correct?
Thanks,
Me
I have a situation where an outside firm is completing some AC power audits on various panels. They have comeback saying that every panel surveyed will need to be upgraded.
The basis for this statement is their method of calculating the loads. The person making the calculations says that NEC requires the circuit to be loaded no more than 80% of its OCP value. (ie - 20A breaker can not exceed a 16A load) This I agree with when sizing OCP devices and wire. However, when it comes to a load study, I am more interested in the actual values rather than what the circuit can handle. Thus, if a circuit is protected by 30A breaker, and the connected load is only 17A. The 17A should be used in the calculation, not 24A.
Any opinion on this?
Conversely, the same problem with the service. I have always understood that the service should not be loaded to more than 80% of its rating. Can anyone point out a NEC reference for this? I am at a loss. The loading is actual load, not calculated load correct?
Thanks,