Hi, good day everyone. I just had an argument with an electrical contractor about the distance of a service receptacle to a service equipment. I tried to explain to him that the service receptacle distance will be based on “Wall Space” since that is what the code says on dwelling units but it didn’t mention to use it on other areas like “Electrical Room”. As from what I understand, as per NEC 210.63 “Service Equipment requires a service receptacle to be located within the same room or area as the service equipment and no further than 25 feet.” is that the distance of service receptacle to the equipment shall no further than 25ft or 7.5m and it’s measurement shall based on “wall space”. I have attached a link for the pciture ----->
.
Can you verify if I am correct or not? I just really want to close this issue. Thank you and God Bless us all.