210.63. I need a service GFCI for a split unit 208 with neutral.
I know I can't go off the load side of the disconnect...but could I use one phase and the neutral (same circuit feeding the HVAC equipment) for the GFCI?
Tap at the line side of the HVAC unit disconnect to feed the service gfci? Basically eliminating the need to pull a separate 12/2 for the GFCI?
I know I can't go off the load side of the disconnect...but could I use one phase and the neutral (same circuit feeding the HVAC equipment) for the GFCI?
Tap at the line side of the HVAC unit disconnect to feed the service gfci? Basically eliminating the need to pull a separate 12/2 for the GFCI?