Service receptacles 210.63

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The inspector has noted very few service receptacles installed near major equipment
This is a very large industrial facility. The engineering firm has located 120V duplex convenience receptacles at approximately 100 feet apart. However it did not install specific Service Receptacles. If a large piece of equipment doesn’t specifically require 120V, why would they need to be installed?


Sent from my iPhone using Tapatalk
 
If this is a industrial space then 210.63(B) would apply which does not have the 25' requirement that exists for dwellings.
 
The inspector has noted very few service receptacles installed near major equipment
This is a very large industrial facility. The engineering firm has located 120V duplex convenience receptacles at approximately 100 feet apart. However it did not install specific Service Receptacles. If a large piece of equipment doesn’t specifically require 120V, why would they need to be installed?


Sent from my iPhone using Tapatalk
What type of equipment?
 