Re: Service Rigid Pipe
Originally posted by earlydean:
<snip> What we see in the pics are enclosures rated for outdoor use being embedded in the structure. <snip>
How do you mean? Are you saying they're not UL rated to be buried in the stucco or wall?
Residential main panels come four ways:
1. Surface only.
2. Flush only.
3. Semi-Flush only.
4. Surface with semi-flush adapter option.
#2, #3, & #4 are UL listed and designed to only go in the wall. The only way to pipe into them is in the wall.
Thanks to this forum I'm already squared away on the fact that supersurface SE meets the NEC. My comment above was to say that
previous to this forum I did not know that SE supersurface was an NEC approved method. I didn't mean for anybody to take it personally or blow a gasket. Read my post again. I said "I stand corrected".
Are there any other states besides CA that use semi-flush or flush meter-mains, meter bases or meter-main/combos?
On a one-story house with a 2' overhang, with an overhead drop, the corner eave is about 9' off the ground. PoCo regulations require the drop to be 10' (or more) off the driveway. The only way to get it up is with a periscope. The periscope has to penetrate the roof membrane. We can't put a main breaker in the eave (too high-- must be 6'-7" or less) so we drop down to 6'-7" or less. Somebody said once you penetrate that roof membrane you're in the building envelope. What's the difference if it's in the wall, or outside of the wall if it's in RMC?
I'm not seeing the prohibition in the NEC, and in fact with the 6'-7" rule we have to drop down-- we can't put the main breaker in the eave.
Again, I see the NEC as being purposely vague and leaving the call to the AHJ about putting the pipe in the wall or going supersurface.
If you look at an electrical plan, the roof penetration and the disconnect will be zero feet apart if you drop straight down with the pipe. Getting back to the OP, that's probably why the AHJ in question is bi***ing about that 24" offset in the drop.
I'll have to study up on the CEC and see if there's any special amendment, but it's a non-issue for me.