2 answers to questions you did not ask but might be options:
1. You do have the option of a 175A main breaker. In such a case, many electricians (oh no, not me...

.) don't even do load calcs, they figure 175A covers 99.99% of 200A service loads.
You would need to finnagle your 80A PV output down to 65A though. (65A PV + 175A main brkr = 240A)
Remember you are allowed to use individual inverter output amps when adding them..... instead of adding individual inverter breaker sizes. This helps if there is considerable rounding up.
Sometimes a smaller micro inverter does the trick, with surprisingly minimal to no peak shaving losses.
Details.....
2. Do you actually have a 225A bus? That opens up a whole new world. That means 70A PV ......w/o downsizing nuthin.
Or 95A PV with a 175A main breaker.
E.g. many EATONs are 225A today.