wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Agreed, I would answer 125A based on 215.2(A)(1)(a). There's no scoping limitation in the question, so all of the NEC is fair game.For instance, leaving the issues raised in the OP behind, if I were to ask what is the minimum feeder capacity for a 100A continuous load . . . I would imagine you could provide an answer.
Now if the question is "what is the minimum feeder capacity for the load calculated in accordance with Part III, IV, or V of Article 220?" followed by a list of loads which add up to 100A after relevant demand factors, I would say 100A, without inquiring about continuous vs non-continuous. Because the scoping restriction in the question limits us to Article 220, which never uses the phrase "continuous load" and has no 125% factors.
Cheers,
Wayne
P.S. Tangent: I think the NEC would be clearer if it deleted the sections on sizing conductors based on 125% of continuous loads (or replaced them with fine print notes). It is enough to have the sections on OCPD stating that except for 100%-rated OCPD, they must be sized based on 125% of the continuous load served. The 240.4 requirement that conductors be protected not exceeding their ampacity (with some exceptions) would still cause the conductors to be sized based on 125% of continuous loads. But the reason for the requirement, namely the limitations of OCPD, would be clearer.
One notable small consequence of this change would be that a 48A continuous load (e.g. an EVSE) could be wired with #6 NM cable (limited to 60C ampacity of 55A) on a 60A OCPD (using the next size up rule, 240.4(B)). As far as I can see, that would be a reasonable optimization and poses no safety issue. [And if I'm mistaken on that last point, then I would like to know, and would withdraw this suggestion.]