The only concise requirement I can think of is regarding supply side connection (i.e. ahead of service disconnect). 705.12(A), second sentence:where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array![]()
You should find that the only requirements on service size (unless you are making a line-side tap to connect the PV as mentioned above) will be those set by POCO as part of your interconnect agreement with them.where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array![]()
The number you need to start with is the next standard OCPD rating up from 125% of the maximum rated AC output current of your inverter(s), not the DC power rating of the PV array. Are you talking about a backfed breaker in a panel or a supply side tap? If it's a backfed breaker you need to look at 705.12(D)(2), colloquially known as the "120% rule". If it's a supply side tap, then the ceiling is the size of the service.where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array![]()
Really not trying to pick nits, but in odd circumstances you could end up satisfying the 120% rule and still exceed the service rating when using backfed breakers. So even in that case there is still the requirement that the number not exceed the rating of the service.The number you need to start with is the next standard OCPD rating up from 125% of the maximum rated AC output current of your inverter(s), not the DC power rating of the PV array. Are you talking about a backfed breaker in a panel or a supply side tap? If it's a backfed breaker you need to look at 705.12(D)(2), colloquially known as the "120% rule". If it's a supply side tap, then the ceiling is the size of the service.
Sorry, but I have to disagree. 705.12(A) only applies to a supply side connection.Really not trying to pick nits, but in odd circumstances you could end up satisfying the 120% rule and still exceed the service rating when using backfed breakers. So even in that case there is still the requirement that the number not exceed the rating of the service.
Since adsmith may be starting from a zero knowledge state, I wanted to make the answer more complete.![]()
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array![]()
OK, so the NEC may not require it, but I do not know of any POCO that will not balk at a PV output larger than the service size, regardless of how it is connected.Sorry, but I have to disagree. 705.12(A) only applies to a supply side connection.
I'll agree with that.OK, so the NEC may not require it, but I do not know of any POCO that will not balk at a PV output larger than the service size, regardless of how it is connected.
where would i find the code requirements for an appopreatly sized service that would support a 24kw pv array![]()