Typically on every project i always start with giving the utility a call to see what their max peak demand is over 12/mo. This will tell me the max demand a specific facility has drawn over a given interval; winter heating, summer cooling and busy seasons..
We have a federal government project that has its entire building backed up by a 400 KW gen. Existing HVAC is Electric cooling and gas heating. They want to go to electric heating. If I used the peak demand given from the utility (metered in June = summer month) and summed up the estimated heating load its over their service capacity.
I've been told another option would be to take the max peak during winter months instead since heating is intended to be removed. Not sure if this is standard practice or if there's a better way to do it. Just seems like its doing a bit of hand waving and making assumptions. Bottom line, if winter months peak cannot be used new service, generator, ATS's.... all need to be replaced which would be $100,000's. I dont want to raise any red flags unless its certain.
Thanks,
We have a federal government project that has its entire building backed up by a 400 KW gen. Existing HVAC is Electric cooling and gas heating. They want to go to electric heating. If I used the peak demand given from the utility (metered in June = summer month) and summed up the estimated heating load its over their service capacity.
I've been told another option would be to take the max peak during winter months instead since heating is intended to be removed. Not sure if this is standard practice or if there's a better way to do it. Just seems like its doing a bit of hand waving and making assumptions. Bottom line, if winter months peak cannot be used new service, generator, ATS's.... all need to be replaced which would be $100,000's. I dont want to raise any red flags unless its certain.