Service Switchboard Size

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
So riser says this service switchboard is 2500A and the schedule says 4000A as you can see. Obviously a mistake I'd imagine.
They are calling for (6) sets 600A based on that 2500A seems correct. Not sure why schedule indicates 4000A
 

Attachments

  • Capture.JPG
    Capture.JPG
    388.1 KB · Views: 24
  • Capture1.JPG
    Capture1.JPG
    39.5 KB · Views: 27
  • Capture2.JPG
    Capture2.JPG
    61.8 KB · Views: 26

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
600 kcmil=420 amps*6=2520 amps, nowhere near 4000 amps. Your third graphic clearly indicates a 2500 amp OCPD.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Probably a lazy engineer cutting and pasting old specs would be my guess.

Sent from my BE2028 using Tapatalk
 

Charged

Senior Member
Location
Ohio
Occupation
Electrical Designer
The MDP schedule is generated from the revit software. That format is generic format when you don’t do much to it. I usually generate one to see what the loads are coming in at but let the single line do the specifying. Typically I don’t do a schedule if I have all the loads and overcurrent protection devices on single line. My guess is they were using it for load calc and didn’t mean to put it on drawings or were careless when doing so. Send RFI if that’s possible to verify.
 