OK I'll preface this by saying I know that you cannot simply add up the size of the OCPD but does something about this seem odd?
In reviewing the service switchgear drawings I found this. I have a 4000 amps service with no main and these switch/OCPD combinations.
Switch #:
1) 3000 AS/2500A Fuse
2) 3000 AS/2500A Fuse
3) 3000 AS/2500A Fuse
4) 4000 AS/3500A Fuse
5) 3000 AS/3000A Fuse
All of the feeders are full sized based on the OCPD in each service disconnect. Other services have similar setups. My gut tells me something isn't right. Opinions?