OK I'll preface this by saying I know that you cannot simply add up the size of the OCPD but does something about this seem odd?
In reviewing the service switchgear drawings I found this. I have a 4000 amps service with no main and these switch/OCPD combinations.
Switch #:
1) 3000 AS/2500A Fuse
2) 3000 AS/2500A Fuse
3) 3000 AS/2500A Fuse
4) 4000 AS/3500A Fuse
5) 3000 AS/3000A Fuse
All of the feeders are full sized based on the OCPD in each service disconnect. Other services have similar setups. My gut tells me something isn't right. Opinions?
Switch #: