- Lockport, IL
- Semi-Retired Electrical Engineer
I am performing an independent review of a design package. The building has a second service (300 amps) for standby loads. I am OK with that. The same service provides power to both legally required standby and optional standby loads. I am OK with that too.
Here is my problem with the design. The designer is bringing 310 amps worth of service conductor into the building. The conductors are then spliced within a junction box, from which 200 amps worth of wire is run to a 200 amp fused disconnect, and 100 amps worth of wire is run to a 100 amp MCB panel. The two overcurrent devices are close enough to each other to be considered “grouped,” and we are within the “2 to 6 disconnecting means” limit. But the requirement for overcurrent protection for service conductors doesn’t say you can downsize the wires that lead to each of the “2 to 6 disconnecting means.” I would call this a poor design, but I can’t find a code article that forbids it. If the 310 amps worth of wire came from an upstream panel that had a 300 amp breaker protecting the wire, then we would be within the 240.21 tap rules. But those rules apply to tapping a feeder, not a service.
Is this proposed design code compliant? Why or why not?