An existing building has a 37.5 KVA, 120/240V, single phase service transformer, and a 200 amp MCB panel. I am reviewing a design that intercepts the service conductors just inside the building wall, installs what they are calling a "pull box," connects a set of #1 wires to the existing service conductors, and runs them to a new 100 amp MCB panel. This seems wrong on many levels. But I will start with, "are we allowed to tap a service"? I know that if they made the connection at the transformer secondary, kept the existing 200 amps worth of wire to the 200 amp MCB panel, and ran 100 amps worth of wire to the new 100 amp MCB panel, they would not be overloading any wires. They might have an issue with two services to the same building, but that's another matter. As shown, they appear to want the existing 200 amps worth of wire to supply both panels, at least up to the location of the pull box.
What do you think?