I believe 230.90 Exception 3 covers that,
:thumbsup: Thanks!
Last edited by a moderator:
I believe 230.90 Exception 3 covers that,
230.46, yes
Which is what I meant to say earlier, but I was unknowingly looking under the "underground service conductors" section. You have the correct reference.
For instance,
I could see where the main panel could be drawing nearly full load and the 100 amp subpanel drawing only a fraction of it, and tripping out the 200 amp main if you do the subfeed thing.
Where as if you had tapped the service conductors in this same scenario, you would still be within the limits of the main, and the Service Conducors, and, no problems would occur.
That doesnt make any sense, unless the SEC are rated over 200A for some reason. If the 200A is tripping, moving some of that load to the line side of the 200A breaker doesn't change anything other than allow you to overload the SEC!
. . . "are we allowed to tap a service"?
I can't quite get here from there. That article points you to four other articles that essentially address means and methods. But they do not have rules similar to the feeder tap rules that include requirements for conductor sizes (as compared to the conductor being tapped), distance limits, and overcurrent protection at the end of the tap. Even if I knew the AWG size of the service conductors and the distance between their new pull box and the new panel, how could I judge whether the installation would meet all relevant NEC requirements, especially as I don't know where any such requirements would be found?230.46, yes
I can't quite get here from there. That article points you to four other articles that essentially address means and methods. But they do not have rules similar to the feeder tap rules that include requirements for conductor sizes (as compared to the conductor being tapped), distance limits, and overcurrent protection at the end of the tap. Even if I knew the AWG size of the service conductors and the distance between their new pull box and the new panel, how could I judge whether the installation would meet all relevant NEC requirements, especially as I don't know where any such requirements would be found?
I am still looking at this as a "non-trivial exercise."
If the 200 amp panel is drawing say 150 amps, and,you subfed the 100 amp panel from the 200 amp panel, and, the 100 amp panel is drawing 50 amps (200 amps total), and, the service conductors are rated at 200 amps, you will most likely trip the 200 amp breaker even though you haven't overloaded the 200 amp rated service conductors if run this way for any length of time.
In that same scenario, with a service tap, you would not trip the 200 amp, and, you still would not have overloaded the 200 amp rated service conductors.
JAP>
You said that so much better than I, lolAlso as old sparky said, perhaps you could get into a game with using the 90 degree ampacity for the common SEC, as long there werent any 75 degree terminations on them.
Ok well fair enough. I admit I would not sleep well at night having a 200 amp breaker with 199 amps on itAlso as old sparky said, perhaps you could get into a game with using the 90 degree ampacity for the common SEC, as long there werent any 75 degree terminations on them.
Its got nothing to do with sleeping well at night.
Just clarifying that I did make sense even though you didn't think I did, I think.![]()
JAP>
Would the connection violate 230.82 because it is connected to the supply side of the service disconnecting means?
I can't quite get here from there. That article points you to four other articles that essentially address means and methods. But they do not have rules similar to the feeder tap rules that include requirements for conductor sizes (as compared to the conductor being tapped), distance limits, and overcurrent protection at the end of the tap. Even if I knew the AWG size of the service conductors and the distance between their new pull box and the new panel, how could I judge whether the installation would meet all relevant NEC requirements, especially as I don't know where any such requirements would be found?
I am still looking at this as a "non-trivial exercise."
Would the connection violate 230.82 because it is connected to the supply side of the service disconnecting means?
Kind of curious why no one has commented on this that I posted:
It is the violation of 230.70(A)(1) in my opinion. If the tap box is outside, no problem, if it is inside then the disconnect(s) aren't "nearest the point of entrance."
All of the discussion about tapping is moot in light of this. Unless you all disagree with this interpretation.
Kind of curious why no one has commented on this that I posted:
It is the violation of 230.70(A)(1) in my opinion. If the tap box is outside, no problem, if it is inside then the disconnect(s) aren't "nearest the point of entrance."
All of the discussion about tapping is moot in light of this. Unless you all disagree with this interpretation.
the distance has been addressed in this thread several times the state in question allows 15 ft to meet that requirement
That is extremely generous and far outside the allowance here,