cschmid
Senior Member
- Location
- Northern cold country
you will learn allot here..dang that Bob always making you look up stuff..he he
cschmid said:dang that Bob always making you look up stuff..he he
iwire said:
My old school teachers would find this quite ammsuing......they could not get me to look up anything. :grin:
Infinity,infinity said:This is a simplified version of our basic routine:
....
4- Install a fused drop with GFCI protection for temp power at drop
...
15- Get cold beer
While we're waiting, I can tell you about the one I made. I started with four 50a alligator clamps with heavy-duty rubber boots, and a length of 12/4 rubber cord.Energy-Miser said:Could you please tell me more about step 4 above?
Energy-Miser said:Infinity,
Could you please tell me more about step 4 above? My guys are always complaining about running out of battery power in their power tools.
Thanks, this is very useful. e/m.LarryFine said:While we're waiting, I can tell you about the one I made. I started with four 50a alligator clamps with heavy-duty rubber boots, and a length of 12/4 rubber cord.
I cable-clamped this into the top of a 2-pole W/P breaker box, nippled into a 4" sq. with two GFCI receptacles. This is all attached to a 1x6 with a hanger hook on top.
I'll see if I can make some pix.
Thanks, just checked out your photo posts, impressive array of tools and pretty specialized. e/mmdshunk said:It might involve using something like #6 in my photo:
OK whats #9 & # 10 ???mdshunk said:
cadpoint said:OK whats #9 & # 10 ???
Click on the "My Photos" link, it will have a lot more pics, with explanation of each including the two you are asking about. Very nice really. e/m.cadpoint said:OK whats #9 & # 10 ???
Energy-Miser said:Click on the "My Photos" link, it will have a lot more pics, with explanation of each including the two you are asking about. Very nice really. e/m.
Hey! That last panel has a bus-mounted main breaker. If it's not marked line-load, couldn't it be used in those cases where someone wants to supply a greater-than-125a sub-panel feeder?
How are all of those branch circuit cables secured to the panelboard?
Neither of those panels would pass inspection here.
Each panel has clear 312.5(C) violation and IMO very likely 312.5(A) as well.
4- Install a fused drop with GFCI protection for temp power at drop
220/221 said:By the lugs?:smile: They are not secured to the panel but they sure as heck aren't going anywhere. They enter thru a plastic snap in bushing. That's they way we do it here. It is safer than using connectors which compress the wiring which can damage the cable over time.
220/221 said:It is safer than using connectors which compress the wiring which can damage the cable over time.
Heh heh, this aint there.
I gotta give you C but A is purely subjective. The reality is that the cables can't go anywhere.
Let me see if I can post it here for you:480sparky said:"My Photos" Link???? I'm confustigated again.....:-?
Not securing the branch circuit cables in that manner is a violation of the NEC. Do you have a local code that permits this or do your inspectors not look very closely?
I think 'A' is more about keeping any sparks and flames inside the panel if there is a fault.
Strange.....that does not seem to be a problem for the rest of us.
I did not see the violations in the first panel but I did see the violations in the second panel..dont know how you would correct the problem in the second panel but I do believe you would have to sleeve it in the block..
The one thing that I don't see is fuse protection for the drop. We have a drop made up that has a 20 amp fuse and GFCI protection. I'll see if I can post a photo.mdshunk said: