Is there room in the panel to put in a 3-pole 20A breaker to power a 20/2 208V circuit that's tripping? Just like the 50/3 breaker you mentioned above, the 20A 3-pole breakers don't have a load neutral connection. So as I mentioned earlier these 3-pole breakers would not need a "grounded neutral" detection function. So if you substitute in a 20A 3-pole breaker and it doesn't trip then that would lend credence to the hypothesis that the grounded neutral detection function in the 20/2 breaker is falsing and causing it to trip, and it's not caused by ground fault leakage on the load side.
If the 50/3’s aren’t tripping, I’m almost certain the 20/3’s won’t trip either.
If I had a constant grounded neutral downstream, the breaker wouldn’t hold. It’s for that reason I haven’t pulled every grounded conductor and checked continuity back to the neutral bar.
But......
I just had what may be a giant light bulb moment.
I made the utility pedestal taps myself. After we were energized, which was maybe 7-10 days later, the job foreman told me the lineman came to tell him the connections were wrong.
Duke left me four 750’s in a pedestal, one unmarked black, and the other three had a colored zip tie in red, blue, white.
Now I’m having flashbacks to the time another utility energized my neutral on a job once because they use white, red & blue as phase conductors.
So now I’m willing to bet they energized my neutral bus on this job. If so, then it’s highly likely all of these breakers are damaged.
#%$@