I'm upgrading a service from 400amp 208volt 3 phase to 600amp 208volt 3 phase. I'm using 2 sets of 350kcmil thhn wires paralleled in 2 raceways. I calculate the adjusted ampacity of each set to be 560amps. Can you please explain to me why this is acceptable for a 600amp service?
Because each each raceway has 4 current carrying conductors.
Wouldn't each conductor derated to 80% current carrying capacity equate to 280amps? If so, wouldn't the parallel set equal 560?