No, 83% of 200A is 166A. 1/0 copper is only good for 150A. 3/0 is what it would be without an allowance. So 1/0 is definitely too small.So I take 1/0 copper or 3/0 aluminum for a 200 amp service is within code?
So for the in between values they do not apply becuase without the 83% adjustment 4/0 al is 200 amp ok . But with 83 %No, 83% of 200A is 166A. 1/0 copper is only good for 150A. 3/0 is what it would be without an allowance. So 1/0 is definitely too small.
The 3/0 Al is also too small.
So 1/0 copper is rated 175 a, but not up to the next value say 175 to 199 ? All of the in between values which you get with 83% rule ?No, 83% of 200A is 166A. 1/0 copper is only good for 150A. 3/0 is what it would be without an allowance. So 1/0 is definitely too small.
#1/0 copper is rated for150 amps at 75° C not 175 amps.So 1/0 copper is rated 175 a, but not up to the next value say 175 to 199 ? All of the in between values which you get with 83% rule ?
The 170 amp value for 1/0 copper is for 90 degrees C, you can use it for starting point for ampacity adjustments (presuming you have 90 C insulation)This has nothing to do with the 'next size up' rule.
In most situations you must use the 60 or 75 degree temperature rating for building wiring; that 170 value for 1/0Cu is their to tease you,using most common materials in most situations you end up using 150A as the ampacity for 1/0Cu.
Jon
When they took the table away a few years back they wanted us to apply ampacity adjustments before coming up with a final conductor size, the old table didn't factor any adjustments but the values in the table were 83%. Now 2020 brings the table back but look at the table - it is posted in post 5, it has a note at bottom saying those values only apply when there are no adjustments necessary. I didn't look at 2020 content, but am guessing if adjustments are necessary they still want you to use the 83% value after adjustments are made.
That applied to derating for conductors on a roof.related to this I recall that if you used XHHW or SE cable containing XHHW for the service drop you do not have to derate for temperature under any conditions. I recall reading this in an older code book (2017?) but can't find it in 2020. Am I nuts?
Correct. In Phoenix, when I was doing services, you had to use 3/0 CU for 200A because of the temperature correction. Here in Texas, you can follow that table with no adjustments needed.
That's correct. 310.15(B)(7) is specifically for "Single-Phase Dwelling Services and Feeders".So for structures that are not dwellings, such as barns or commercial buildings, the 83% rule does not apply ?
I'm doing this from memory. I think the design temperature was 104F.Is that because Texas is on a different code cycle? Or is that because Phoenix has a hotter design temperature? I think of both those places as hot, and would expect similar results with required temperature corrections.
4/0 Copper? That's some overkill, I would be grumbling about that guy as I tried to manipulate it.One year, some ding-dong SRP engineer was going to make a name for himself and we had to use 4/0 for 200A services. This went on for about 6 months before someone got it changed back.
Can you confirm that you take the size of the overcurrent protection device, and not the load demand calc on a panel to apply the 83% rule. I have an existing 150 amp panel with a 2/0 AL. wire. Appliances were added and the new load demand on the service is 140 amps. So do you apply it to 150 x .83= 124.5 amps or 140 x .83= 116.2 amps. I am trying to identify If I can keep the 150 amp panel with a 2/0 AL. wire or I need to upgrade to 175 amp 3/0 AL wire#1/0 copper is rated for150 amps at 75° C not 175 amps.
Take the size of the service OCPD and multiply by 83% then go to Table 310.15(B)(16) and find a conductor that has at least that value. That would be the minimum conductor size.
For example 300 amp service:
(300*83%=249 amps), then Table310.15(B)(16) so either 250 kcmil copper (255 amps) or 350 kcmil aluminum (250 amps).