Thank you. I guess I will be telling the client she needs to upgrade. Thank you for your response.You would use 150 amps not 140..
Thank you. I guess I will be telling the client she needs to upgrade. Thank you for your response.You would use 150 amps not 140..
There are two things involved, the size of the service required and the size of the conductors. A load calculation tells you the minimum service size. The 83% rule tells you the minimum conductor size for that service.Can you confirm that you take the size of the overcurrent protection device, and not the load demand calc on a panel to apply the 83% rule. I have an existing 150 amp panel with a 2/0 AL. wire. Appliances were added and the new load demand on the service is 140 amps. So do you apply it to 150 x .83= 124.5 amps or 140 x .83= 116.2 amps. I am trying to identify If I can keep the 150 amp panel with a 2/0 AL. wire or I need to upgrade to 175 amp 3/0 AL wire
Why would you need to upgrade?Thank you. I guess I will be telling the client she needs to upgrade. Thank you for your response.
You need at least 140 amps of capacity (presuming you did calculations correctly) you likely not finding a 140 amp breaker so you will be going with minimum of 150 amp breaker. If you do so you can use that 83% factor on 150 amps to select a conductor. Should you decide to go with 175 or 200 amp breaker then you apply that 83% to 175 or 200 when selecting a conductor - whether the calculated load is 140, 45, 125, or 173Can you confirm that you take the size of the overcurrent protection device, and not the load demand calc on a panel to apply the 83% rule. I have an existing 150 amp panel with a 2/0 AL. wire. Appliances were added and the new load demand on the service is 140 amps. So do you apply it to 150 x .83= 124.5 amps or 140 x .83= 116.2 amps. I am trying to identify If I can keep the 150 amp panel with a 2/0 AL. wire or I need to upgrade to 175 amp 3/0 AL wire