I got a bid to wire machinery shop and storage building. 200 amp 1 phase service. THe customer wants no light flicker whatsoever. The power company I thought was going to bring a pad mount xfmr within a 100 ft of the building. This would help with voltage drop. Now they want set a pot on a pole across the street, run 1/0 triplex overhead to a jump pole, and have me run 225 ft to this jump pole. I have spec'd 250 kcmil to this jump pole. Is there anyway to figure out the voltage drop on all the wires. Will a standard calculation work. The poco says up size the wire accordingly. But when they supply with 1/0 aluminum, I feel it kind of defeats the purpose for us to spend more money on larger wire, when it might not alleviate any problems. Any suggestions or solutions?