We are getting ready to install a 200AMP 277/480vac service. The power company asked that Meterbase be mounted next to the utility power transformer. I have always mounted the meterbase next to the service equipment. However, in this case the service equipment is located at a small building about 75FT away from the utility transformer.
1. Is there a maximum distance requirement between the meterbase and the service equipment?
2. Do we still treat it like the meterbase is next to service equipment and drive ground rods at the service equipment with a bonding conductor back to the meterbase?
3. A NEC code reference would be helpful.
I just haven't done it this way but I'm sure it has been done before.
1. Is there a maximum distance requirement between the meterbase and the service equipment?
2. Do we still treat it like the meterbase is next to service equipment and drive ground rods at the service equipment with a bonding conductor back to the meterbase?
3. A NEC code reference would be helpful.
I just haven't done it this way but I'm sure it has been done before.