I'm feeding a panel 120/208v. from a breaker in a meter stack. The meter stack is supplied by a 400 amp breaker where the ground and neutral are bonded. Do I need to run 4 wire and also another ground rod or 3 wire and bond the neutral and ground also to a ground rod. THANKS
You will need to run 4wires and keep the ground and netural seperated. Since you are coming off of a breaker, the breaker is the first source of disconect and everything after that the ground and netural is seperated.