service
Dennis Alwon said:
I would appreciate that info.
No problem, I want to see it again as well......maybe I put my foot in my mouth....either way if I find it I will post it.:smile:
I can't open pdfs on the PC that I am using right now....it's an old one that chokes on pdfs.:rolleyes:
OK here it is from the 2008 ROP regarding the use of Table 310.15(B)(6).
Short version....
Panel Statement: The panel agrees that the present wording is ambiguous. It is the panel’s intent that this allowance apply only to conductors carrying 100% of the dwelling unit’s diversified load.
Long Version....
6-61 Log #194 NEC-P06 Final Action: Accept in Principle
(310.15(B)(6))
____________________________________________________________
NOTE: The following proposal consists of Comment 6-40 on Proposal 6-41
in the 2004 May Meeting National Electrical Code Committee Report on
Proposals. This comment was held for further study during the processing
of the 2004 NATIONAL ELECTRICAL CODE. The recommendation in
Proposal 6-41 was:
Revise as follows:
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders.
For individual units of one family, two-family and Multifamily dwelling
units, conductors, as listed in Table 310.15(B)(6), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors, service
lateral conductors, and feeder conductors that serve as the main power
feeder to a each dwelling unit and are installed in raceway or cable with
or without an equipment grounding conductor. For application of this
section, the main power feeder shall be the feeder(s) between the main
disconnect and the lighting and appliance branch-circuit panelboards(s).
The feeder conductor to a dwelling each unit shall not be required to be
larger than their service-entrance conductors. The grounded conductor
shall be permitted to be smaller than the ungrounded conductors,
provided the requirements of 215.2, 220.22, and 230.42 are met.
Submitter: Frederic P. Hartwell, Hartwell Electrical Services, Inc.
Recommendation: Accept the panel action in principle. Clarify the
permissible application of the multiple feeder allowances as one of the
following four options:
1) “… the main power feeder shall include the feeder(s) serving only loads
associated with a single dwelling unit and running to but not originating in the
lighting and appliance branch-circuit panelboard(s) serving the dwelling unit.”
OR
2) “… the main power feeder shall include the feeder(s) serving only loads
associated with a single dwelling unit and running to the lighting and appliance
OR
3) “… the main power feeder shall include the feeder(s) serving only dwelling
loads and running between the main disconnect and the lighting and appliance
OR
4) “… the main power feeder shall include the feeder(s) serving only dwelling
loads and running to but not originating in the lighting and appliance branchcircuit
panelboard(s) serving a particular dwelling unit.”
Substantiation: By clarifying that this note applies to dwelling units within
multifamily housing, which is well advised, the proposal raises important
questions as to exactly which panelboard feeders are within the scope of this
allowance. Options 1 and 2 exclude feeders that are comprised of dwelling
loads, but that serve multiple dwelling units. Options 3 and 4 allow such a
feeder. Options 1 and 2 as a group and options 3 and 4 as a group sort out
whether this allowance applies to subpanel feeders within a dwelling unit.
Dwelling unit subpanel loads do not present the same diversity as dwelling unit
panels serving the entire dwelling unit, and thereby undercut one of the
traditional supporting assumptions underlying these allowances. However, all
of these interpretations are possible given the ambiguous “(s)” endings on the
word “feeder” and “panelboard.” CMP 6 needs to clarify exactly which feeders
qualify for this allowance.
Panel Meeting Action: Accept in Principle
Remove the 2 sets of parentheses and the duplicate “s” on panelboards so that
the section reads:
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For
individual dwelling units of one family, two-family, and multifamily dwellings,
conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt,
3-wire, single-phase service-entrance conductors, service lateral conductors,
and feeder conductors that serve as the main power feeder to each dwelling
unit and are installed in raceway or cable with or without an equipment
grounding conductor. For application of this section, the main power feeder
shall be the feeder between the main disconnect and the lighting and appliance
branch-circuit panelboard. The feeder conductors to a dwelling unit shall not be
required to have an allowable ampacity rating greater than their serviceentrance
conductors. The grounded conductor shall be permitted to be smaller
than the ungrounded conductors, provided the requirements of 215.2, 220.61,
and 230.42 are met.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Thanks for all the input. I am using the A&B buss off the 400 amp panel for the main house only. This panel (milbank) supplies two seperate 200 amp breakers with flange kit included 650.00 I am using the other 200 ocp for the guest house it is only a 60 ft run in pvc underground so to pull the #6 ecg would be inexpensive, but what purpose would it serve?
I really think getting rid of those duplicate "s" and parenthesis to make the word panelboard as a singular will do much to help this article.
Thanks for the info Bob.
Interestingly-- if I run USE cable in the ground with no raceway to another dwelling then this article won't apply. Am I correct? Do you know why?
If you use a 4 wire feeder then the egc would act the same as it would in a sub panel. You would need to separate the grounds and neutrals and bond the gec to the egc not the neutral.
I believe in 2008 you will have no choice but to run a 4 wire feeder to a detached building. So-- I would do it now-- especially if there are metallic pathways between th buildings like pnone , cable or copper water lines. Read art. 250.32(B)