Hello, Can I use eight 500 kcmil T.H.W.N per phase for a 3000 amp 480/277 volt service or do I need to count the neutral as current carrying and increase to 600 kcmil?

Thanks
 

bob

Senior Member
Location
Alabama
teco said:
Hello, Can I use eight 500 kcmil T.H.W.N per phase for a 3000 amp 480/277 volt service or do I need to count the neutral as current carrying and increase to 600 kcmil?

Thanks
Is this in an underground duct bank?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What type of load do you have? IMO it's really unlikely that a load would have more than 50% harmonic current, therefore the neutral is not a CCC.
 

Joe Villani

Senior Member
I agree with Trevor on this one. You should be to go.

However before installing these conduits, you might want to check with you AHJ requarding those conduits travelling 15' into the building without overcurrent protection. Some jurisdictions have very tight requirements with respect to 230.70 (A) (1). You might want to put them in the slab or cover them with at least 2" of concrete.



Joe Villani
 

raider1

Senior Member
Staff member
Location
Logan, Utah
teco said:
Thanks Chris. It is 310.15b4c that makes me think I needed to increase to 600 kcmil.

Your welcome.

Does the load really consist of more than 50% non-linear?

I agree with Trevor and Joe, check the load to see if you really have that much non-linear harmonic loading.

Chris
 

teco

Senior Member
Location
Mass north shore
Thanks Joe. These conduits will be run from under a pad mount up a rear outside wall then along the wall for about 15'. They will enter the main breaker directly upon entering the building.

Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
teco said:
Thanks Joe. These conduits will be run from under a pad mount up a rear outside wall then along the wall for about 15'. They will enter the main breaker directly upon entering the building.

Thanks

Sounds like you are good to go.
 