Re: service
Originally posted by petersonra: You have 200A available on each hot leg for a total of 400A of 120V.
Originally posted by coulter: So I question him a little, and he says, "Well it's 330A per phase, and that's about 1000A total."
I tried once to discourage this manner of describing current flow. I would like to try to discourage it again. For the single phase example, 200 plus 200 equals 200; it does not equal 400. For the three-phase example, 330 plus 330 plus 330 equals 330; it does not equal 1000. As Dave Barry was wont to say, ?I swear that I am not making this up.?
Here is how the math works (single phase example):
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Put 200 amps of 120 volt load on the left-hand (even-numbered) breakers of a 120/240V panel.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Put 200 more amps of 120 volt load on the right-hand (odd-numbered) breakers of the same 120/240V panel.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The left-hand side has 200 amps times 120 volts, or 24,000 watts of load. Please note that load is power, it is not current.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The right-hand side also has 200 amps times 120 volts, or 24,000 watts of load.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The total load is 24,000 watts plus 24,000 watts, or 48,000 watts.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The total current associated with this total load is 48,000 watts divided by 240 volts, or 200 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">QED