OK, when i went to school, a whopping year a half ago, my instructor told us that the main grounding electrode should be either the metal building frame or cold water pipe, and shall be supplemented by either a rod or other means. But recently i was told by an inspector that the rod is the main electrode, and a water pipe is a supplemental, she said thats what the code says. but i read today in 250.53(d) (2) that
when cold water pipe is used a supplementing electrode of a rod or ring or other type shall be used in conjunction with
Am i right about the water being the main or a rod???
I know AHJ is always right...lol jk...but i still wanna know if i stand a chance on running #6 to my ground rods and 4 bare to my main cold water [/code]