necbuff

Senior Member
I rejected a service mast riser today that had a die cast set screw connector screwed into a rigid coupling that was on the end of a stick of rigid. The joint was between the stand off brackets and had an approx 4' piece of rigid on the bottom. Kind of hard to explain but I do not know how to get a picture into this site. He said I was picking on him and has called all the brass. They are going to look at it monday> I don't see how anyone can think this is OK. It is plain in 230 and RMC articles (don't have book in front of me). Any thoughts?
 
Re: set screw fitting on service mast riser

230.28 Service Masts as Supports.
Where a service mast is used for the support of service-drop conductors, it shall be of adequate strength or be supported by braces or guys to withstand safely the strain imposed by the service drop. Where raceway-type service masts are used, all raceway fittings shall be identified for use with service masts. Only power service-drop conductors shall be permitted to be attached to a service mast.
Seems pretty clear I doubt that a die cast set screw connector is identified for use with service masts.
 
Re: set screw fitting on service mast riser

Yes it is. As I stated before, this is a no brainer per Art 230 and as you stated in RMC. Hopefully a picture is coming.
 
Re: set screw fitting on service mast riser

For what its worth, we do not permit any fittings between the roof and the service head and we require 2" rigid metallic conduit if we hit the mast for a service. :D
 
Re: set screw fitting on service mast riser

For what its worth, we do not permit any fittings between the roof and the service head and we require 2" rigid metallic conduit if we hit the mast for a service.

Charlie, is this a local ordinance? I also have always used 2" GRC as a mast attachment because the POCO's requested it. Then I saw someone use a 1 1/2" GRC as a mast and it passed. There seems to be a gray area as to what adequate support means when it comes to conduit and wire span.
 
Re: set screw fitting on service mast riser

It can only be objectional to the POCO,Thet would etermine what mast will carry there line weight and dynamic load.Computers for dummies :D
 
Re: set screw fitting on service mast riser

Oh forgot should have been 1st is the weather head UL listed ?
 
Re: set screw fitting on service mast riser

Pictures From NECbuff.

kennyservice1.jpg


kennyservice2.jpg


Kenny how can the installer even question you on this?

As Pierre pointed out set screw fittings are not rain tight.

I think the problem is this contractor can not thread 2" RMC. They took the job they should be able to do it right.

They have at least a few options.

1)Buy a threader

2)Rent a threader

3)Run to the local home depot and they will thread a 2" for you. You might have to buy the 2" RMC from them to do so.

Bob

[ September 11, 2004, 11:41 AM: Message edited by: iwire ]
 
Re: set screw fitting on service mast riser

344.42 Couplings and Connectors.
(A) Threadless. Threadless couplings and connectors used with conduit shall be made tight. Where buried in masonry or concrete, they shall be the concretetight type. Where installed in wet locations, they shall be the raintight type. Threadless couplings and connectors shall not be used on threaded conduit ends unless listed for the purpose.
IMO even with the small overhang and the connector upside down it is still a wet location.
 
Re: set screw fitting on service mast riser

The mechanical strength of this connections bothers me more than the fitting being listed as raintight. Are threaded rigid couplings listed as raintight? I have seen a number of installations that water has entered the raceway through threaded rigid connections that were wrench tight. The only way water is going to enter the EMT fitting is if it is being sprayed up from the bottom. Neither the meter socket nor the loadcenter are designed to prevent water from entering through the bottom. If I was the installer I would have threaded a short section of RMC as Bob suggested.
 
Re: set screw fitting on service mast riser

In the first pic, it looks like the drop has already been installed and connected. Around here POCO will not install drop without approval from AHJ.
 
Re: set screw fitting on service mast riser

The contractor did not have to thread the 2" GRC, all they had to do was measure the mast length, cut off the top of the riser, then the weatherhead clamps on 2" GRC. Yes 10ft of 2" GRC is more expensive than a 10ft stick of 2" EMT, but now you have egg on your face, you have lost wages, which by the way is a contractors most expense, and you have a Red Tag against you !!!.........all for the cost of maybe $30 ???
 
Re: set screw fitting on service mast riser

Originally posted by dduffee260:
The contractor did not have to thread the 2" GRC, all they had to do was measure the mast length, cut off the top of the riser, then the weatherhead clamps on 2" GRC.
Yeah you could do that but IMO having the service supported by the coupling is kind of shaky. That is just my opinion and not code. :)

Originally posted by dduffee260:
Yes 10ft of 2" GRC is more expensive than a 10ft stick of 2" EMT,
It is all GRC now, that is a die cast set screw GRC connector.

You can not use EMT on a mast. :)
 
Re: set screw fitting on service mast riser

Looks like GRC to GRC,is the M.A.listed to go into a GRC coupling?Or is it an E.M.T. fitting
.
 
Re: set screw fitting on service mast riser

Well I am not there so I can not say for sure that is not an EMT fitting.

But Die Cast Set Screw GRC / IMC connectors are available.

Here is one company that makes them.
 
Re: set screw fitting on service mast riser

This die cast connector is listed for EMT/IMC/ RMC. But not a wet location. I forgot to mention the service drop is 109' long and is coming from across the road.
 
Re: set screw fitting on service mast riser

I agree with Bob. Putting the 10? section on the bottom and the short section on top is asking for problem. The chance of the coupling splitting or the conduit breaking at the coupling is very good.

I have never seen die cast fittings for RMC. The only set screw and compression fittings for RMC the suppliers stock in my area are steel. Bob, did you notice that in the link you provided the only rigid fittings available were for 1/2?, 3/4? and 1?? They don?t have any fittings for 1 ? - 2?. Once you get to the 2 ?? sizes EMT and RMC are the same OD.

Kenny, are you sure that the fitting was listed for EMT, RMC & IMC? I don?t see how one fitting could be listed for different OD pipes.

Another question?..How is this set screw fitting any less rain tight than the weather head? The only way I can see water entering this fitting is from the bottom but water will also enter the weather head from the bottom.
 