e57
- San Francisco, CA
You make the call - is it wall space - does it count?
For ref' heres the wording....
Existing fixed window, new floor surface, but existing structural floor in a high rise (typically local AHJ wont force existing walls or surfaces to meet current codes - so there is often a point to aurgue...) - but new walls wrapping a column. The column is away from the window, but wrapped it back to the start of the window. Is it wall space?
(1) Spacing. Receptacles shall be installed such that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.
(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers such as freestanding bar-type counters or railings