SEU as Feeders

Status
Not open for further replies.
Re: SEU as Feeders

You question is not clear, you mention "feeder" and "unfused". A feeder is "fused" and a service is not.

It may not be a NEC issue, but a local rule. In Washington State unfused service entrance conductors of any type are limited to 15 ft.
You can always concrete encase the SEU and go as far as you want.

[ February 10, 2004, 12:26 AM: Message edited by: tom baker ]
 
Re: SEU as Feeders

230.70(A)(1)The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
 
Re: SEU as Feeders

This is purposly left unspecified by the NEC. Each AHJ must be allowed to inspect each individual service to determine what is "nearest the point of entrance" for each building. However, everyone agrees that no service conductors are to be installed hidden within the building structure; the SEU must be visible for its entire length. Any rules of thumb, like 5 feet, 10 feet, or 15 feet, are arbitrary. I'll wager that any utility or state has not commited to writing a specific length. For, if they did, they would have opened a large legal "can of worms".
 
Re: SEU as Feeders

By the way, the rule of thumb is measured from where the wire enters the building. The portion within the structure needs to be kept to an absolute minimum.
 
Re: SEU as Feeders

230.6 Conductors Considered Outside the Building.

"... or inside nearest the point of entrance of the service conductors."

I have no problem with bringing service conductors anywhere you want inside a building, as long as they are encased in 2 inches of concrete as 230.6 states.
How some of these municipalities have come up with 10, 15 or more feet I do not know - I would make sure that is in writing.
Why does one need to enter so far into a building with the service conductors without overcurrent protection? The only answer I can see is MONEY!

Pierre
 
Re: SEU as Feeders

Pierre
I have seen the results when the service conductors short out and in one case it was in the concrete slab about 2" in. the slab cracked and shorted the SEU the heat it generated exploded the concrete and caught the carpet and couch on fire (just smoldered). The wire burned all the way to the outside wall exploding the concrete along the way. what stoped it was the tap on the secondary at the transformer finely melted open. The only thing that saved this house was that the carpet and couch had flame retardent as required by the manufactureing codes. SO I don't go into a house very far even when the local AHJ will allow it. unless there is OPCD's for it.
 
Re: SEU as Feeders

Originally posted by earlydean:
However, everyone agrees that no service conductors are to be installed hidden within the building structure; the SEU must be visible for its entire length.
I would have said that too until Bill A. steered me to a thread at his site.

Here is a picture of a typical CA service.

The service riser runs down the inside of the wall to a flush mounted meter panel combo.

FPE_Service.JPG
 