This is purposly left unspecified by the NEC. Each AHJ must be allowed to inspect each individual service to determine what is "nearest the point of entrance" for each building. However, everyone agrees that no service conductors are to be installed hidden within the building structure; the SEU must be visible for its entire length. Any rules of thumb, like 5 feet, 10 feet, or 15 feet, are arbitrary. I'll wager that any utility or state has not commited to writing a specific length. For, if they did, they would have opened a large legal "can of worms".