seu cable indoors

Status
Not open for further replies.
Thank you for the advice Dennis. I can put it on a 50amp breaker but not a 60amp.
Next time you need anything in Ala Cty give me a shout.
Well, it would depend. If you have alumininum then #4 is rated 55 amps at 60C. If the calculated load is 55 amps or less you may go to a 60 amp breaker based on 240.4(B)
 
Thanks I owe you one. My knowledge base only consists of chickens, tesla coils, politics, philosophy, wood burning stoves & rc airplanes though.
 