W wire monk Member Jun 22, 2009 #1 Is it a code violation to install SEU in 2" rigid pipe for a service riser. Are do the conductors need to be seperate.??
Is it a code violation to install SEU in 2" rigid pipe for a service riser. Are do the conductors need to be seperate.??
raider1 Senior Member Staff member Location Logan, Utah Jun 22, 2009 #2 SEU can be installed in a raceway. It can't be installed in a raceway underground though, take a look at 338.12(A)(2) (2008 NEC) Chris
SEU can be installed in a raceway. It can't be installed in a raceway underground though, take a look at 338.12(A)(2) (2008 NEC) Chris
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jun 22, 2009 #3 wire monk said: Is it a code violation to install SEU in 2" rigid pipe for a service riser. Are do the conductors need to be seperate.?? Click to expand... You can install seu in a riser but since this is a complete raceway you would have to check your conduit fill. It probably is not an issue but you should be aware of it.
wire monk said: Is it a code violation to install SEU in 2" rigid pipe for a service riser. Are do the conductors need to be seperate.?? Click to expand... You can install seu in a riser but since this is a complete raceway you would have to check your conduit fill. It probably is not an issue but you should be aware of it.